> [@This is why i hate cobalt ss drivers](https://forums.speedlife.net/t/this-is-why-i-hate-cobalt-ss-drivers/27102/118):
>
> The only time that the freeon charge would be an issue on it not runnin would be in a very high end condensing unit that would have a low pressure switch.
> 
> If pressure within system drops too far it would open the switch not allowing the control circuit to be completed. wich prevents the unit from running

A vast majority of new units (within the past 3 years or so) have both high and low limits on them, especially those with Scroll compressors that they are concerned will burn up even on a very small change in freon level.

---