So in our server room we have the following outlet, It says 30A but I think it’s a 20A. I’m not an electrician so I don’t know if that even makes sense:
the plug(in your hand) says 250v on the plug so that wont work in the receptacle in the wall regardless of what plug you get (since that is a 125v outlet). so i would verify the voltage on the UPS. if it is 250v youll need a new line ran from a 250v panel to supply power to that
edit: just saw you noticed the voltage difference. you need to verify the voltage on the UPS first off and then go from there. if its only 125 then get a new plug. if its 250 you need an electrician to come in and wire a separate outlet
<EDIT>
Just went back to past emails. Not only did we Specify that we had an L5-125 receptacle, we sent a picture of the actual outlet and asked for a UPS solution to match. We got a L6-250V connector. Dey Done Goofed.
You have an L5-30R on the wall. That receptacle contains Hot - Neutral - Ground conductors. The hot wire will be terminated to a 30A single pole breaker. The ground and neutral to the neutral bar. Because you only have the option of going HOT to NEUTRAL you only have the potential of 120V, not 240.
The L6-30P That is pictured is made to work with HOT - HOT - GROUND. This would be terminated back to a 2 Pole 30A breaker and the green wire to the neutral bar. This is how you get 240. Two legs of the 120A 180* out of phase = 240V potential.
No adapter will ever work for the above reasons.
Here is the solution. You need to purchase an L6-30R, a 2p30A breaker for your panel, and some red tape. The cable should contain BLACK - WHITE - GREEN conductors. In the panel you will wire the black wire to one pole of the new breaker, and the white wire will be taped red and wired tothe other pole. The only remaining wire on the neutral bar is the green. In the junction box you will wire the black and “red taped white” wire to the hot terminals of the new receptacle and the green to the ground terminal.
Voila.
Also, DON’T DO ANY OF THIS. I am not responsible for you killing yourself when you touch the bus or something.
Thank you sir! Doing an adapter was 100% not what I wanted to do at all. I’d rather have a licensed electrician come in and toss the correct receptacle into the ceiling an call it a day. The closest electric work I’ll be doing is plugging this thing in. We also are a tenant of a building so I gotta get it approved first (shouldn’t be a problem). The problem is/was that we sent them pictures and the specs of what we had and they send us the wrong plug. It’s also the biggest UPS they make before needing to A)hardwire it directly into the panel or B)Split the load (<lol) over 2+ UPS units.
Here’s some pictures of the setup to get a better understanding. I figured if I needed electric parts I’d throw some business your way @tpgsr and I could just swing by and pick it up. Again, I would rather not use any type of converters or adapters to jerry rig this thing to work. http://imgur.com/a/Et0wS